We are submitting a LEED v4 BD+C NC project with LEED v4.1 upgrades on a credit-by-credit basis. Minimum and Optimize Energy Performance have remained v4. We are interested in pursuing the v4.1 WE – Optimize Process Water Use credit via Option 2 methodology of comparing to a baseline model, however, we have modeled the building under ASHRAE 90.1 2010 Standard. Are we eligible for credit achievement using the ASHRAE 90.1 2010 model, in lieu of creating a second model (modeled to ASHRAE 90.1 2016) solely for the purposes of credit achievement?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $12.95 »
Marianne Vajstedt
LEED ConsultantGeniMac inc.
3 thumbs up
January 11, 2022 - 4:29 pm
I have the same question as Deb Favaretto. Additionally, what are the requirements on the results of the energy model?
The credit EA Energy Performance remain under LEEDv4 and ASHRAE 90.1-2010.
Afogreen Build
www.afogreenbuild.comGreen Building Consultant
137 thumbs up
February 15, 2022 - 1:00 am
Hi Deb,
If you choose a credit under LEED v4.1, then you should follow all the credit requirement under LEED v4.1. The v4.1 WE – Optimize Process Water Use credit via Option 2 requires to model baseline system using ASHRAE 90.1-2016, then you should do it. You can check first whether any discrepancies between ASHRAE 90.1-2010 and ASHRAE 90.1-2016 in term of baseline model.