Forum discussion

NC-v4 EAp1:Fundamental commissioning and verification

OPR & BOD & Design Document review

Fundamental Commissioning requires the CxA to review the OPR and BOD and design documents.

Why does the Fundamaental Commissioning LEED Online template require the CxA to list the "Date of CxA review of CONSTRUCTION documents"?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/04/2022 - 23:04

That's one of several inconsistencies I've noticed in this credit that haven't been addressed in addenda.
The credit language also indicates the Cx Provider develops the OPR and BOD. In the next paragraph, we just review them.
If you ask ASHRAE, we review it, we verify it, we may even provide a format for it but we're not responsible for creating it.
​https://www.ashrae.org/file%20library/about/new%20hq/ashrae-opr-attachment-to-design-services-rfp-signed.pdf

Wed, 08/09/2023 - 23:03

Yeah I'm confused by the credit language as well. Is the design team responsible for reviewing the OPR? Is that first created by the owner rep so that the design team can review? Is the design team responsible for creating the BOD