FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Opaque Doors vs Doors with Glazing Vs Windows

What is the proper way to represent a door which happens to have glass? According to 90.1, doors that are more than one-half glass are considered fenestration. So in a program like HAP, should all of the doors with more than 50% glass area be entered as windows or do you still enter them as doors with a U-value for the opaque portion, plus a separate U-value and shading coefficient for the glazed portion? If the glass area is less than 50% of the door area, is the glazing U-value and shading coefficient governed by different minimum requirements than if the glass area was more than 50% of the door area? Let's say you have a 21 sqft metal frame entrance door with a small 1.3 sqft sight glass in it. Would the glass portion requirements be dictated by "Metal framing (entrance doors)" under Fenestration in Tables 5 of 90.1? Would the rest of the door be dictated by Opaque Doors "Swinging" then? What if the glass area in that example was more like 18 sqft of the door? Would it be treated any differently?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/01/2013 - 15:54

Doors are modeled as doors and windows as windows. Doors with glass in them would be modeled with the glass in the door and either an overall assembly U-value or modeled separately as glazing and framing.

Fri, 11/01/2013 - 16:01

So what is the significance of 90.1 considering a door with more than 50% glass to be fenestration? Regardless of the amount of glass content, all doors are modeled as doors?

Fri, 11/01/2013 - 16:06

The impact would be related you your previous question on vertical glazing area and the 40% maximum. They define fenestration as not being opaque. So the glass in the doors counts as glazing area but a door is still a door.

Fri, 11/01/2013 - 17:04

Ok, thanks!

Mon, 09/30/2019 - 22:11

Hi Marcus,    I am going to piggyback on the above question for  additional clarification on modeling HM doors on the perimeter of the building. The opaque doors are not labelled and therefore considering to use the following U-factor value from A7.1: "Insulated metal swinging doors, including fire-rated doors, insulated access hatches, and insulated smoke vents: 0.50" 1) Installer provided a certificate stating that with 1.75 inch thickness for the unlabelled HM doors with R-26 Rockwool insulation inserted under the hats and between the ribs of internal steel stiffeners, it's U-0.13. Is there any additional information should be asking them to support this claim, so I don't have to default to using the 0.50 U-factor per Appendix A7.1?    2) There is a variety of HM door types from Corridors leading to MECH rooms and bathroom, that I intend to model. These HM doors have features such as "kick plates  with louvers". Is it necessary to model these interior doors considering temperature differential in these spaces? Thank you in advance.  

Tue, 10/01/2019 - 20:54

U0.13 sounds like a point calcualtion. U0.5 sounds much more reasonable and realistic for an overall value. You don't need to model the interior doors, especially if the spaces are adiabatic and air just flows through them.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.