CI-2009 EAp2:Minimum Energy Performance

Occupancy Sensor

We have a project which has a big " function" area . this particular area is for employees to hang out + meet up with customers + briefing area (with a formal meeting table, projectors). do we need to install an occupancy sensor in this area? This space is about 1900 SF.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/09/2011 - 17:08

Jason, it sounds like your multi-purpose room will require an occupancy sensor based on ASHRAE 90.1-2007 Section 9.4.1.2 Space Control.

Tue, 05/10/2011 - 03:16

Kim, i'm confused, because, i have 2 project which been awarded with gold and the other with silver but we did not installed any occupancy sensors at this "function" area.

Tue, 05/10/2011 - 12:23

Jason, if your "function" area is enclosed by ceiling-height partitions and is classified as a classroom, conference/meeting room, or employee lunch/break room, and you're following the 90.1-2007 compliance path for LEED 2009, you'll need an occupancy sensor in that space (unless the function space has multi-scene lighting control).