NC-v4 SSc6:Light pollution reduction

No outdoor lighting?

We have a project that has no exterior lighting - not even emergency egress, as the travel paths go through an existing, compliant building.
Does this mean we comply with the credit, or is it "not applicable"?

Thanks in advance!

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/01/2022 - 18:11

From what I remember, zero outdoor lighting will earn this credit.  Note in the message area that there are zero outdoor lights in the scope of this project. But you may have to add 1W when filling out the form or the software will think the form is incomplete and won't allow you to submit. 

Fri, 04/01/2022 - 18:42

Will do. Thanks for the prompt response Bill!  

Tue, 02/10/2026 - 12:24

Ahh... I was also facing this issue. The 1W trick still works.___________________Alexandrahttps://ndrelectric.com/