Hi,

I am working on the certification of a wharehous, in V2009 version.

The wharehouse only counts with ventilation, and no cooling or heating systems. 

As per ASHRAE 992.1-2007, Appendix G, Table G3.1, Nº 10 HVAC Systems, c) the heating system classification shall be assumed to be electric, and th system characteristics shall be identical to the system modeled i the baseline building design, and as per d) the cooling system shall be identical to the system modeled in the baseline building design.

As per Table G3.1.1A, Baseline HVAC System Type for a Nonresidential Building and 3 Floors or Less and < 2300 m2 (because the conditioned space is  0 m2), and electric heating, the Baseline System would be System 4 - PSZ-HP.

Is this assumption right?,

Thank you.