Forum discussion

CS-2009 EAc1:Optimize energy performance

Night-Setback also in Baseline?

THE BMS in our project is programmed with a night-setback function to reduce the temperature at NO operation (night) in winter for energy saving purpose. As the temperature setpoints have to be modelled the same in the Proposed and Baseline my question is, if a night-setback function via BMS has also to be modelled in the Baseline Case. Or does it qualify for additional energy savings and is just to be modelled in the Proposed Case?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/11/2012 - 13:27

The temperature settings must be identical in both models for each hour of the year. See Table G3.1.1#4. Temperature set back is not eligible for additional energy savings.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.