LEED Reviewers are implementing new requirements for the baseline building (LEED NC v2.2 EAp2 VAV System) through the comment process. In the last three reviews, I have received comments that the Fan Energy (kWh) / Fan Power (kW) should be around 3,000 hours. For a check, I simulated the "Ref Bldg Large Office New2004_v1.3_5.0" with Chicago weather file. I reset the minimum flow rate to 0.40 cfm/ft2 (0.00203 m3/s/m2). The results are 1039.43 GJ and 79047 Watts in fan energy and fan power. This calculates to 3,652.6 hours which exceeds the new requirement for a well-known reference building. To achieve this new requirement, you must reduce the minimum flow rate or turn off the fans during setback or both. It seems unreasonable. New LEED requirements should be reviewed through public process and based on scientific research. New LEED requirements should be implemented through the next publication with LEED reference guide. Or, perhaps I’m missing something…