Forum discussion

NC-2009 EAc4:Enhanced refrigerant management

Nee of a fire suppression system

Hi all, Currently we are working on a project which does not have a fire suppression system, but is trying to achieve "Enhanced refrigerant management" credit in LEED NC 2009. In the LEED online form for this credit there is a option to mark "Fire suppression systems in the project do not use ozone-depleting substances (CFCs, HCFCs, or halons)." As the project does not have a fire suppression system we kept this field unmarked, but then the LEED online form shows incomplete. Does this mean that a project must have a fire suppression system to earn this credit? Thank you

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/06/2017 - 13:46

Magda, just tick this box and in "additional details" - "special circumstances" just write that there is no fire supression system. the intent of the credit is not to use CFC, HCFCs and halons, so if you don't have fire supression system at all you meet the intent of the credit. In the reference guide it states"do not operate OR INSTALL fire supression system that contain ozone-depleting substances(...)". regards,

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.