HI, The client requesting to have DX air conditioning system for each space in the building. My questions: 1. Could I use the sliding door as operable wall/window to supply the fresh air? 2. Do we need to concern about the fresh air to the other rooms which do not have the conditioning system? Thanks in advance

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/10/2015 - 15:01

Yes, sliding doors can be used as operable windows to meet the 4% min; however, you must also verify that these and other openings are at least 25' away. If not those areas will require mechanical ventilation or a combination of mechanical & natural to comply.