According to ASHRAE 62.1 - 2010 User's Manual, example 6-AF, the requirement associated with controls that guarantee that the openeings remain open during occupancy can be met with an administrative policy. Does this mean that the provision of ASHRAE 62.1 -2010 (section 6.4 exception b.1), "controls that prevent the openings from being closed during periods of expected occupancy", can be complied with a mandatory administrative procedure / policy ?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Christopher Schaffner
CEO & FounderThe Green Engineer
LEEDuser Expert
962 thumbs up
June 13, 2017 - 1:30 pm
No.
Ricardo Sá
Director of SustainabilityEdifícios Saudáveis Consultores (503 910 767)
84 thumbs up
July 3, 2017 - 10:16 am
Can you please clarify why not?
Christopher Schaffner
CEO & FounderThe Green Engineer
LEEDuser Expert
962 thumbs up
August 31, 2017 - 2:26 pm
A policy is not a control. Although it is not defined in the standard, I read "control" to mean something automatic.