Hello,

I am doing a pre-assessment for an existing building with only natural ventilation. As the reference guide refers, I'm using ASHRAE 62.1-2007, paragraph 5.1. However, the paragraph about interior spaces without direct openings to the outdoors was not so clear to me regarding their required distance to the outdoors (operable walls or roof openings).
Does an interior space without any direct openings to the outdoors but adjoining a room with a direct opening to the outdoors (complying 4% rule) also have to be within 25 feet of operable wall or roof openings to the outdoors? For example, there's an interior space (20 feet by 20 feet) which is ventilated through an adjoining room (25 feet by 25 feet and complying 4% rule) and the openings between rooms are permanently unobstructed and have an area of more than 8% of the area of the interior room. But, the depth of the adjoining room (which is open to outdoors) is 25 feet. So, if I measure the distance of the interior room from the outdoors by using the adjoining surface of the interior room, it is 25 feet and complies with standard. On the other hand, if I measure the distance of the interior room from the outdoors by using the farther side of the interior room, it comes out to be 45 feet from the outdoors and it does not comply with the standard.
1. Which one is correct?
2. If it does not comply with the standard, what can be the alternative strategies in order to be able to comply with the standard and be eligible for LEED-EB certification?