With the removal of the M&V credit under LEED V4.0, is a calibrated energy model still required under Fundamental Commissioning and Verification credit or some other LEED credit?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Paul Swierc
Senior Commissioning Agent20 thumbs up
December 2, 2015 - 6:15 pm
MKK,
With eliminating the M&V credit, V4 is moving toward Monitoring-based Commissioning (EAc1, Option 1, Path 2) and Advanced Energy Metering (EAc3) as a means to monitor and verify energy performance during building occupancy. Neither of these credits, nor the Fundamental Commissioning and Verification prerequisite (EAp1) will require a calibrated energy model.
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
December 4, 2015 - 1:14 pm
Paul is correct, M&V as it was known in v2009 no long exists, but in its place are a series of three credits that provide the foundation for robust measurement and tracking of energy use. Involving the CxA in design of the on-going monitoring systems is a great step, as during the process they see the kinds of trends that are needed to ensure proper operation of the systems. I always called these key parameters, and worked with the owners and integrators to make sure if these parameters were changed, over-ridden, or went outside certain bounds, that some notification went to the management for investigation.