We are working on a residential building where split AC units are provided in every room for each unit with no mechanical ventilation. The ventilation strategy is relying on natural ventilation through operable windows.
Regarding the natural ventilation monitoring requirements in LEED v4, none of the options seem feasible in our case, since exhaust fans are only installed for toilets and kitchen hood.
Does anyone have experience with similar projects that can share what is the best strategy for ventilation monitoring in naturally ventilated residential buildings?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Steve Loppnow
YR&G1 thumbs up
September 14, 2017 - 1:27 pm
Mario,
This is fairly new territory for all of us, so I'll share a few thoughts despite not having an answer. First, I would submit the question directly to USGBC via the LEED Coach email address and include your project number. As I read the requirements, if you are using an exhaust ventilation scheme, then you would need to monitor that CFM, not OA in the exhaust system (kitchen and bathrooms), which seems doable? Why wouldn't monitoring the exhaust system be feasible? The first and third bullet under naturally ventilated spaces on page 606 of the BD&C RG seem reasonable, but the second one does not. All of that said, I'm not finding any comparable requirements for monitoring in the Homes RG, and in my limited experience in dealing with v4 residential ventilation, USGBC has been leaning toward ASHRAE 62.2 and the Homes requirements when questions arise about how to deal with MF ventilation requirements in v4. If you are meeting ASHRAE 62.2 in the units, you should be ok, but follow-up with USGBC to confirm, and specifically call out any concerns about monitoring requirements.
Nancy Henderson
Managing MemberArchEcology, LLC
83 thumbs up
September 14, 2017 - 8:45 pm
Hi Mario,
I recently ran across a LEED Interpretation #10461 that provides an exception to the monitoring requirement for systems that have an outdoor intake flow of 1000 CFM or less. That does not entirely answer your issue though. The new version of 62.1-2010 requires mechanical ventilation when natural ventilation is not available - so if you are not going to provide supply ventilation, then you need your bath fan to also serve as a whole house fan and provide ventilation when the windows are closed. The source of make-up air is also something to consider depending on your local code requirements. We have been using two speed fans in these situations. The fans run continuously at low volume (30-40 CFM depending on the size of the unit) for whole house ventilation and then have a built in occupancy sensor to ramp up to a higher flow rate when the bathroom is occupied.
Sherman Aronson
Sr. AssociateBLT Architects
4 thumbs up
January 22, 2020 - 5:45 pm
See below info from the LEED User intro to this credit. This is a big topic for multi-family residential that intends to use windows for code compliant ventilation. Perhaps it is possible for oversized bath exhausts to work, but how does the outside air get into each unit? That becomes a mechanical ventilation system? Thanks.
The prerequisite has different compliance paths for mechanically ventilated and naturally ventilated spaces, and you may need to follow both paths for the same building on a space-by-space basis. In fact, teams should beware that ASHRAE 62.1-2010 effectively prohibits natural ventilation via operable openings as a stand-alone strategy. This is because the standard requires spaces to be mechanically ventilated whenever the operable windows are closed. Multifamily residential buildings may be most impacted by this type of scenario.
David Posada
Integrated Design & LEED SpecialistSERA Architects
LEEDuser Expert
1981 thumbs up
January 22, 2020 - 7:44 pm
LEED Residential – Multifamily requires ASHRAE 62.2, not 62.1 for dwelling units. For ventilation of dwelling units to meet minimum IAQ requirements under LEED Homes Multifamily Midrise (per 62.2) we've typically seen four general strategies accepted by USGBC in our region/ climate (Pacific NW, Climate zone 4C, Marine):
Operable windows alone may meet code for ventilation in some jurisdictions but doesn’t meet LEED Homes or NC. In all cases you’ll need to consult with a mechanical engineer to ensure the equipment or passive vents can provide sufficient air flow. Providing outside air via an under-cut entry door from a pressurized corridor hasn’t been allowed under any version - poor odor & noise control, hard to ensure adequate air flow.
We’ve found LEED Homes for Midrise v3 and v4 (which in some cases have been allowed for high-rise projects) to be a better fit for multi-family residential projects than LEED BD&C NC v2, v3, v4. The new LEED Residential Multifamily rating system in 4.1 appears to be merging the Homes and NC programs, but being so new I can imagine more uncertainty about the requirements and compliance paths.
For example, I’m baffled by the 4.1 requirement “Makeup air systems must have a means of closure and be automatically controlled to start and operate simultaneously with the exhaust system.” That seems to eliminate trickle vents. That might be the intent given the thermal comfort issues in colder climates, but in milder climates they might make sense.
Since 4.1 is a draft version, and they say “We appreciate any feedback on the current draft content,” here’s an opportunity for input!