FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Modelling Baseline Envelope for Existing + Additions

Dear forum users, I have modelled a project following Appendix G. and have received a review regarding my interpretation of % glazed area on the baseline. The project is a mayor renovations + Additions (existing conditioned warehouse + New office building attached). There were no modification on % area of vertical and horizontal glazing on the existing bit of the building. My approach was to model existing envelope, shape and fenestration, exactly the same in both proposed and baseline. The addition was modelled following the "maximum 40% for vertical fenestration and 5% for skylight" rule. The result of the whole building for baseline is, 28% vertically glazed and 12% of skylights (the existing bit was very different than 40%, and 5% respectively) The reviewer states that the end result for the baseline should still be 40% and 5%. It is not very clear to me how would I get there.. Do I have to make the existing fenestration proportionally smaller, just like I would do for the baseline of a completely new building? Thanks in advance. Santiago.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/05/2013 - 14:45

Table G3.1-5 Baseline (f) says to model the baseline envelope with the existing conditions prior to the renovation. Table G3.1-5 Baseline (c) says to model the glazing area the same as the proposed or use the limits if the proposed is over those values. It clearly says that this applies only to new building and additions. Table G3.1-5 Baseline (d) related to the skylights does not say it only applies to new construction and additions. I would think the vertical glazing and skylights would be treated the same but that is not the case based on a literal interpretation. So I think you are correct to model the existing vertical glazing the same. Apply the 40% rule to the addition only. The skylight area is not so clear. Our interpretation is that (f) would allow you to model the skylight area the same in the existing and apply the 5% rule to the addition only. This does require some interpretation so the application of the skylight 5% rule is not as clear cut as the vertical glazing.

Tue, 11/05/2013 - 17:37

Marcus, again Thanks. I will reach out to the reviewer to see if we can clarify our approach or need to do the changes they suggested. I posted the same thread on bldg-sim email group and had contradicting opinions about the interpretation on this particular matter, which means there must be room for interpretation. I hope discussions like this one will build into future standards (or whitepapers, and 'how to' guides) so that is less and less dependent on interpretation.

Mon, 02/24/2014 - 11:28

Marcus is absolutely right especially on interpretation on vertical fenestration for additions. So that your "The addition was modelled following the 'maximum 40% for vertical fenestration and 5% for skylight' rule" is right with a not 100 percent certainty on 5% skylights rule (but actually Marcus suggests this 5% rule and LEED reviewer's reply implies this rule as well). But your next statement "The result of the whole building for baseline is, 28% vertically glazed and 12% of skylights (the existing bit was very different than 40%, and 5% respectively) The reviewer states that the end result for the baseline should still be 40% and 5%." seems not clear to me. So in your model, if proposed case for this office addition is 28% vertical fenestration and 12% skylights, the baseline (for just this office addition) should be 28% vertical (minimum of proposed case or 40%) and skylights 5% (minimum of proposed case or 5%). In this case, I don't think you need to model baseline (for this office addition) with 40% vertical fenestration.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.