FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Modeling Toilet exhaust fans

Let's say you have a proposed zone being conditioned by an RTU with only a supply fan and you also have a small exhaust fan exhausting air directly from a toilet room, and that's the extent of your building HVAC systems. What is the proper way to model the toilet exhaust fan power for the baseline? Is it already accounted for in the appendix G fan power calc for the baseline RTU? Or do you add the proposed exhaust fan energy to the baseline model? Or do you do another Appendix G fan power calc just for the exhaust system? Also, does this exhaust fan need to be stated as a separate system in the Tables 1.4 Excel sheet or is it just considered part of the RTU system, even though it's not directly connected to the RTU like a powered exhaust fan would be?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 11/05/2013 - 17:18

The bathroom exhaust is included in your baseline fan power calculation. If it is an exhaust fan serving an unconditioned space then it modeled identically to the proposed.

Tue, 11/05/2013 - 18:18

Understood. Thanks!

Tue, 03/14/2023 - 08:49

Hi there, I wonder if the bathroom exhaust fan shall be included in the energy model or could be calculated on an excel sheet and later added to the totals. Could you share your approach? Thanks

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.