FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Modeling Thermal Zones

I am modeling an office building for LEED which will house different tenants that will consists of a dental clinic and medical clinic etc. There are number of different spaces in the building. When Energy Modeling for LEED how many thermal zones do I need to model. There about 90 spaces and the thermal zones will be 60. Can I use auto zone in eQUEST to create the thermal zones.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 02/13/2013 - 19:21

Section G3.1.1 provides guidance on creating thermal blocks (systems 1 - 4) or whole floor systems (5 - 8) for the baseline system. Table G3.1 - 7 Proposed provides guidance on creating thermal blocks in the Proposed model based on the actual design of the system zoning. You could use the auto zone function to create thermal zones in undefined tenant spaces but in most cases the thermal zones are based on the design of the system and it is not appropriate to use the auto zone function. This is also a feature in the wizard mode which cannot be used to create the final model for LEED which requires you to use the detailed mode. It is OK for your design phase modeling efforts but is not typically used once the design is completed.

Thu, 05/30/2013 - 16:15

Please help me understand G3.1 - 7. In my baseline I have three rooms for a single zone system #3 per G3.1.1B. My proposed I have the same three rooms each their own zone on a bypass VAV system. Do I need to revise my baseline to have a separate unit for each room to have the same thermal zones as the proposed model? I don't meet the exception as stated in G3.1 - 7.

Tue, 06/04/2013 - 13:31

G3.1.1 requires each thermal block to be modeled with its own HVAC system. Basically you match the Proposed thermal blocks. A thermal block is a collection of zones with similar thermal properties grouped together for simulation purposes. If the proposed systems are considered a thermal block then just match that block in the baseline.