FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Modeling HVAC System #8: VAV with PFP boxes

Dear Forum, We are modeling a high rise building in order to comply with EAp2 minimum energy performance. The corresponding HVAC system for the baseline design is system #8, VAV with PFP Boxes. Section G3.1.1 of Appendix G of ASHRAE 90.1 2007 states: For systems 5, 6, 7, and 8, each floor shall be modeled with a separate HVAC system. Floors with identical thermal blocks can be grouped for modeling purposes. So, according to this section, I have to model a VAV system with PFP boxes for each floor (it would have its own chiller, cooling tower, pump and its corresponding air loop). For the project I modeling, this means a lot of work, since we have 23 floors! The floors are not identical in size but have the same thermal zone configuration. Is it acceptable to group them all together? Many thanks in advance

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/22/2013 - 21:47

Your assumption is not quite correct. You model a central chilled water plant for the whole building including towers, pumps, etc.. You model a system per floor (air handling, chilled water coils, electric heat, etc.). So one central plant with 23 systems (unless you can justify lumping some systems together).

Tue, 10/22/2013 - 22:04

Thank you Marcus I got it clear now. In my opinion section G3.1.1 should be explained in more detail because when it says: each floor shall be modeled with a separate HVAC system, it is not clear that it should exclude the central plant. Regards, Santiago