FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Modeling HVAC for future un-designed office space

I am modeling a 50,000 sf college cafeteria that has a basement, a main floor and a mezzanine. A portion of the basement is part of the cafeteria. About 11,000 sf of the basement has been reserved as a future office space that will not be designed or fitted out until a later date and is not part of the design team's scope except as a core and shell space. It will have its own entrance and the using entity will be a department of the college. The cafeteria building will be served by district fossil fuel steam heat, and a cooling tower with condenser loop will serve a number of water-source heat pumps for cooling and heating. The capacities of the heating and cooling loops have been sized to accommodate the future office space loads. The office space does have a separate mechanical/electrical room. The delivery portion of the HVAC system has not been designed, but I think it is unlikely to be designed with a system that does not tie into the systems that will serve the cafeteria. My question arises from reviewing ASHRAE 90.1-2007 Appendix G, Table G3.1 Section 10, as well a few of the posts on this forum. Since the future office space HVAC is not fully designed as part of the project scope, but is within the boundaries of the LEED project, I believe I need to model it as a fully occupied space (according to what I'm reading in forum posts).  Since the HVAC system is not fully designed, it doesn't seem to fit exactly within Section 10b. But since the capacities of the cafeteria HVAC system will, by design, accommodate the future office space, the situation doesn't seem to fit Sections 10c and 10d where no heating system or no cooling system has been specified. Can I autosize water-source heat pumps, similar to others in the building, tied into the heating and cooling loops, and use this as a Proposed Design for the office space? In turn the exact same system(s) would be used In the Baseline model.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/09/2016 - 15:38

You do need to model it as fully occupied. You have the following options when modeling the Proposed system. a. The default VAV system modeled in the Baseline case; the Proposed case modeled with any Dedicated Outside Air Handlers as designed and installed within the base building scope of work, plus a conservative estimate of the fan power and system efficiency for the water source heat pumps. Note: The conservative estimate of fan power and system efficiency for the water source heat pumps may be the worst-case values from manufacturers (Watts / cfm and EER), or the worst-case fan power and efficiency used in the projects in the past five years, or the tenant lease agreement that specifies the worst-case values. ECM motors are not allowed unless included within the tenant lease agreement. b. The default VAV system to be modeled in both the Baseline and Proposed case, with the only energy efficiency measures being cooling tower controls and condenser pump power. c. The default VAV system to be modeled in the Baseline case; the Proposed case to be modeled with water source heat pumps having constant volume fans at ASHRAE 90.1 Appendix G default fan power and system efficiency.