FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Modeling a humidifier in the baseline case

Hi, I am working on a data center project under NC 2009. For the proposed case we have self-contained steam electric humidifiers that are an accessory for the CRAH units; the question is if those humidifiers should be modeled the same in the baseline case, since there is no indication in ASHRAE 90.1 regarding the procedure for modeling humidifiers in the baseline model. The curious issue is that if I model them in the baseline case, they are causing a huge energy consumption in the baseline model because we are modeling economizers (zone 3C) and the zone is very dry (in the proposed model there are no economizers). Id appreciate your guidance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 08/11/2014 - 14:43

I have deleted my original comment after digging into this a bit more. Humidification is considered a process load. As such not only must the process be modeled identically but the energy use must also be identical (i.e. energy neutral). Claiming this savings would violate that requirement. Based on the prescriptive requirements within Section 6.5.1 it appears that exception c applies to your situation. Because of this exception and the fact that the process must be identical you should not be modeling economizer in the areas with humidification in the Baseline.

Mon, 08/11/2014 - 16:56

I have a similar situation in that I will model the humidifier the same in both proposed and baseline systems but in our proposed system we have a DOAS unit with energy recovery which will offer some benefit over the baseline system which is not using an economizer. How would you approach this? Thanks, Mike Edit: mine is not a data center but a museum which has humidification for a few spaces.

Mon, 08/11/2014 - 18:27

Technically you should follow the exceptional calculation method to show process load savings related to humidification. If the savings are relatively small you could probably forego this formality and provide a narrative explanation for the savings and how it was modeled. Some small level of savings related to the systems install and in the baseline should be OK. if the savings are large you should probably do the exceptional calculation. To do so run the models with and without the humidification and show the savings as the difference.

Mon, 08/11/2014 - 22:12

Thank you Marcus, my question is how do I document that exception (not modeling economizer in the areas with humidification in the baseline) if that statement is not part of the appendix G? As far as I know the only exceptions are those included in the appendix G, please correct me if I am wrong. Doing some research I found this on the 90.1 Users Manual regarding the use of humidification and economizers, specifically for the G3.1.2.7: "The drybulb high-limit economizers may increase energy use in dry or cold climates when spaces are humidified. This does not preclude modeling the baseline system with that humidification and economizer..." Id really appreciate your comments. Thank you

Tue, 08/12/2014 - 13:54

That is a pretty clear statement requiring you to model the economizer so I will make another set of suggestions. Obviously ignore my previous advice. You have two choices I think - try to claim the savings for humidification or not try to claim them. If you wish to try and claim them I would suggest that you do it as an exceptional calculation and justify them based on the Appendix G requirements. Doing it this way gives the reviewer a clear picture of what is happening. Personally I think it is a loophole and these savings are not legitimate to claim. The other option is to model the economizer and then just post-process the results. When entering the modeling results in Table EAp2-4 and EAp2-5 enter the proposed energy use for humidification in the baseline so that they are identical. This is the conservative approach and should be accepted.

Tue, 08/12/2014 - 15:15

I had a similar situation which was a computer center/office near Las Vegas which uses a DOAS system and VRF system. The baseline was modeled with an economizer and the required humidity setpoint with autosizing for the humidifier. The proposed was modeled as shown in the contract document with humidity setpoint and the size of the humidifier. It showed a 87% saving in humidifier energy endues. I entered the baseline energy use for the humidifier as shown in the proposed model. I documented the exceptional calculation credit for the remaining energy savings. They rejected the exceptional calculation on the bases for not referencing recently published documents. They also came up with new numbers for the baseline and propose simulation models which I cannot explain. My next project with a humidifier, I plan to model the humidifier as a plug load.

Thu, 08/21/2014 - 20:27

Thanks Marcus for the comments, I've modeled the humidifiers identically and the difference is significant in terms of the humidifier energy use (difference of 87%) but in terms of the energy use of the building it is around 1%. I think this would be safer to include as an exceptional calculation but as far as the documentation that Curtis alluded to that would support what the energy model is calculating, I'm unsure of what would be required? Any suggestions would be great. thanks, Mike

Thu, 08/21/2014 - 20:48

You should provide a thorough narrative that explains how you have modeled the systems and the level of savings being claimed. Make sure to explain why there are savings related to the modeling of the Baseline system as required. The reviewer may still toss out the savings but if you do an exceptional calculation it will be easy for them to make an adjustment.