Hello, Current project has both hardwired permanent lighting fixtures and table lamps plugged into switched receptacles in the hotel rooms of a highrise. Per ASHRAE table G3.1 section 6: b. States proposed building lighting shall meet 9.1.3 and 9.1.4 which excludes plug lighting as they are not permanent fixtures. d. States to include "all" lighting. Exception to d. states to match the proposed and baseline building if the lighting is not shown in the documents; however, they are in the design documents. Baseline says to use lighting power set equal to the maximum allowed for the corresponding method and category in Section 9.2. Proposed b. and d. seem to be contradictory and assuming the base building matched ASHRAE allowable lighting levels, following b. would unfairly cause the proposed building to perform better than reality. Some information I found on the USGBC website seem to suggest the plug fixtures should be included as non-regulated process loads in both the proposed and base building. Any insight/advice would be greatly appreciated. Thank you