FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Modeling Heat Recovering Chillers for the Baseline

Hello,

I want to know which the energy savings are comparing a Heat Recovery Air Cooled Chiller in the Proposed Building versus it´s equivalent in the Baseline Building.

The question is that there is not such a chiller machine specified in Standard 90.1-2007 Table 6.8, so, which would be the best approach model for the Baseline since I have to includ both chilling and heating equipment.

This simulation is not inteded to reflect comfort equipment, just want to know how efficient this recovery chiller is.

Thank you,

 

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/05/2018 - 18:31

The baseline system for comparison is determined by Table G3.1.1A. This selection has nothing to do with the chiller used in the proposed design unless it is also your heating source.

Tue, 06/05/2018 - 19:44

It is my heating source, I am having chilled and hot water simultaneously

Tue, 06/05/2018 - 19:59

Assuming the fuel source is then electric you enter Table G3.1.1A in that column.

Wed, 06/06/2018 - 11:00

Thank  you!