FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Modeling Evaporative cooling systems (ambiator)

Hi all, Iam modelling ambiator for a factory building in India. My baseline system is Packaged VAV. I have few doubts regarding this, 1.Can I consider the ambiators supply CFM as outside air in the baseline model or if I provide the baseline supply CFM to be same as proposed will it be acceptable. If both the ideas doesn't work how can i model this. 2.In the proposed model the unmet hours would be more than 300 hours. Is it acceptable if we write a narrative on the same.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/29/2015 - 07:39

The amount of fresh air for a zone must be equal in both baseline and design case models. Typically, for DOAS, it means zones get a little more air than is usually nessesary as per minimum fresh air requirements such as ASHRAE 62.1. This is okay. The baseline VAV system must bring the same amount of fresh air into the zone as the DOAS. It is a requirement of 90.1 App. G. Why are the proposed model's capacities not enough to meet the setpoint? Either your capacity is too small or your setpoints are not right. A narritive would have to be pretty convincing as to why your case should be handled different.

Fri, 10/02/2015 - 17:05

In a similar climate, Tucson, AZ, evaporative cooling also exceeds unmet load hours on an annual basis. Management and workers accomodate this with more breaks, earlier working hours, shorter days during the hottest season, as we have done for decades, but ASHRAE and LEED allow no exceptions. It is still the most efficient cooling system for a hot, dry climate. We just can't prove it with the existing criteria.

Fri, 10/02/2015 - 17:30

Joyce described schedule adjustments managers and workers make to avoid the hottest part of the day (I just moved to Phoenix, so I understand!). It would definitely require more effort, but close attention to your thermostat and occupancy schedules may help with unmet hours in the situation you describe. If you adjust your occupancy schedules (for proposed and baseline) to reflect the actual building occupancy, such as 6 am-3pm, or with shorter days in the hottest part of the summer, and then schedule the unoccupied hours at a higher setpoint temperature (this part is very important!), you may be able to mitigate the unmet hours in the situation you describe. Also, someone please correct me if I'm wrong, but I don't know of any requirement within the mandatory requirements of 90.1 or Appendix G that require specific thermostat setpoint temperatures. Ensuring your space setpoint in the model reflects the actual operational setpoint, which tends to be higher in our climate than in cooler areas, would also be a good thing to check. I haven't modeled evaporative cooling for a LEED project, so I can't speak specifically to that technology. Best of luck!

Mon, 10/05/2015 - 12:17

Thanks for your valuable comments Jean Marais, Joyce Kelly and Laura Brandt.........got things clear......

Thu, 12/19/2019 - 23:24

We are modeling a factory, there will be no HVAC system only heating and ventilation, the thing is that the ventilation will be supplied by a direct evaporative cooling. Can we assume the proposed system to be Heated only?

Sun, 12/22/2019 - 22:24

You must model the proposed as designed so it must include the evaporative cooling system.

Thu, 03/12/2026 - 04:38

Got this response from GBCI: "Thank you for contacting GBCI regarding a LEED v4 BD+C factory project in Hyerabad with evaporative cooling.1. The baseline ventilation rates shall be modeled in accordance with the minimum requirements of the applicable ventilation code (i.e. ASHRAE 62.1-2010, local code, or the applicable industry standard or guideline for the space type, as applicable), per ASHRAE 90.1-2010 G3.1.2.6 exception (c). The proposed case must be modeled as designed.2. No specific adjustments are required for evaporative cooling systems. For all systems, the calculations must reflect the worst-case operating conditions, meaning the lowest supply airflow rate that can reasonably be expected to occur when each space is fully occupied. 3. The space setpoints must be modeled identically, and unmet load hours must be maintained within limits of Appendix G. It is expected that the conditions maintained within the Proposed case will in a large part be dictated by the outdoor weather conditions. To ensure that similar conditions are maintained within the baseline building model, it is recommended that the temperature setpoint in the baseline case be adjusted to match the maximum temperature maintained during cooling mode within the proposed case model, modified on a monthly basis (or smaller intervals) to better reflect the seasonal impacts on the cooling conditions provided within the proposed case.Note that if the proposed case requires additional mechanical cooling to keep the unmet load hours within the required limits, a cooling system with identical efficiencies to that of the baseline case may be modeled as a supplemental cooling system. However, if the baseline cooling setpoint schedule is adjusted as described above this should not be necessary."


However, can anyone help me with the clarification on why in case of an evaporative cooler, the baseline  OSA shall be as per 62.1 only. My reasoning is that in the proposed case the OSA will act as dehumidifier cfm and this will create a very big difference in the OSA in basecase compared to proposed case. For example, the base case will have around 2 cfm/sqft and proposed will have around 3.5 cfm/sqft.