Modeling energy savings from receptacle load within energy simulation

Hi,

while reading the ID+C guideline (EAp2, p.140) I see that:"Some efficiency measures that no longer need to be modeled using an exceptional calculation method include low-flow water fixtures, kitchen equipment, and kitchen ventilation.

- Low-flow service water-heating fixtures. The flow rates given in WE Prerequisite Indoor Water Use Reduction set the allowable baseline values. Provide sufficient information to justify energy savings from efficient fixtures and appliances that use hot water.

- Kitchen equipment. All project types may count energy savings from efficient refrigeration equipment, cooking and food preparation, clothes washing, and other major support appliances. LEED Appendix 3, Retail Tables 1–4, defines the baseline conditions."

I understand that I can use the nominal values in the appliance datasheet for the proposed building, independently if it is Energy Star or not, and the values in Retail Tables 1–4 for the baseline building, in order to get an additional energy saving in the simulation result, this is valid also for CI and Hospitality projects.

I ask so because,at p. 172 EAc2, this option is mentioned for Retail only projects, while no reference to CI and Hospitality is present.

Secondly, do "Low-flow service water-heating fixtures" include also kitchen appliances or only toilets, showers, taps? Is it possible to quantify a cold/hot water saving and consequently an energy saving from appliances such dishwashers, clotheswashers and so on?

Thank you,

Paolo

 

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/17/2024 - 19:53

You can claim savings for the strategies you describe in a CI project without an exceptional calculation. The low-flow service water heating fixtures are the showers and faucets served with hot water. Flush fixtures are not served by hot water. The savings associated with appliances would include the hot water savings associated with those appliances. In fact the vast majority of savings for dishwashers and clothes washers is already a reduction in hot water usage so you can't double count that.