EBOM-2009 EAc3.2:Performance measurement - system-level metering

Mixed use meter

We have a meter that measures: chiller + pump + lighting system. Since we are not discriminating by "end use": would this meter qualify towards this credit? Thanks GH

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 02/05/2013 - 19:45

Hi Alicia It doesn't appear that this meter would qualify. You would have to meter at the end-use or by the major system type. Thanks Hannah

Tue, 08/13/2013 - 20:42

Hello, My question is very similar to the above: we have 3 main meters, and one is dedicated exclusively to all of the HVAC applications (but does not give a breakdown of each type of system in the HVAC system - FCUs, Closed Cooling Units, Chillers, Chiller Pumps etc.) Assume the following: - HVAC energy use our largest energy use, AND - HVAC energy use is greater than 40% of total energy use. With those two assumptions, we are monitoring 40% of total energy on a separate meter, and we are monitoring greater than 80% of our largest energy use on a separate meter... so would this then qualify for 1 point? Thank you in advance for any advice!

Tue, 08/13/2013 - 20:53

Hi Helen I don't think that the schema you laid out would fly. As a general rule, I try to submit only when heating, cooling and ventilation are separately metered, at a minimum. There may be some instances where this rule wouldn't apply, like where there is a large piece of equipment that would justify being submetered (i.e. a chiller), but generally I stick to the rule. Hannah

Tue, 08/13/2013 - 23:39

Hi Hannah, Thank you for your input. I guess I am confused: why exactly won't this achieve the intent of the credit? Is "HVAC" not considered an "end-use" in it of itself? The credit language requires a breakdown for "major mechanical systems," so wouldn't HVAC be considered a major system? I didn't find any CIRs on this topic. Where would I find the definition of an "end-use," as this was not in the reference guide glossary. Thank you! Helen

Wed, 08/14/2013 - 21:31

Hi Helen, My experience has been that HVAC is not considered a system level end-use and rather that heating, cooling, and ventilation are considered to be system level end-uses. This is supported by the example summary of end-uses in Table 1 on page 200 of the reference guide. Another perspective is that the intent of the credit is to identify opportunities for energy savings. That intent seems to have a stronger correlation to metering systems at a finer resolution rather than having several systems grouped together under one meter.