Min/Max Cooling/Heating air temperatures for ASHRAE 90.1

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 02/12/2011 - 17:39

There are no max/min delivery air temperatures however you must provide a delta T of 20 degrees between supply air and space temperature when modeling the baseline. The energy modeling program will increase the supply volume, which will increase the fan power as calculated per Appendix G.