FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Minimum/Mandatory Requirements for, VAV TU?

I have a Tenant Improvement that has VAV terminal units connected to an existing VAV AHU. The contractor and owner decided to save money and utilize stand alone control. Though the problem with their solution is that the thermostats only have ON-OFF function and cannot modulate between dead band and full cooling (since the project does not have re-heat). I have looked and cannot find much, aside from ASHRAE 90.1-2007 Addendum h, that states that a VAV TU has to modulate. I do not think I am wrong in assuming this control logic, since the opposite is both uncomfortable for occupants and a waste of energy for the tenant. IS IT OBLIGATED THAT THE VAV MODULATE IN LIEU OF ON-OFF (OPEN-CLOSE)? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 07/11/2013 - 14:35

Check out Mandatory Section 6.4.3.1.2 which requires a dead band. Does that help?

Thu, 07/11/2013 - 19:06

Thanks Marcus The deadband covers the minimum, and that is clear and also a requirement to meet ASHRAE 62.1. Though I am not clear how the dead band relates to modulating from 0%-100% and anywhere in between in lieu of ON-OFF. As the system works now, when it is satisfied it goes to minimum. A regular VAV would hover around the current position it is at (X% open)

Thu, 07/11/2013 - 19:08

I don't see anything in the mandatory provisions. Prescriptively there is 6.5.3.2 but that does not appear to address your issue. If there is a requirement in Addendum h then it is logical to assume that the issue is not addressed in the standard.

Thu, 07/11/2013 - 19:58

Thanks Marcus I was in the wrong LEED Guide (my project is GID&C), thus since on this occasion they are not attempting performance compliance, they have to achieve the prescriptive requirements also. Though it is still strange that it is not required for a VAV to modulate for an office environment. I can understand a shut-off VAV for non-occupied spaces. Thanks