The project seeking LEED certification includes air-to-water heat pumps (4-pipe), that are able to produce hot and chilled water (simultaneously or separetly). This type of equipment does not seem to be listed in ASHRAE 90.1 - 2007 tables 6.8.1. My questions are:
1- Can you please confirm that Is this type of equipment is not listed?
2 - Is it exempted of water chilling packages minimum efficiencies requirements as per section 6.4.1.3?
Thanks in adavance
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5867 thumbs up
August 31, 2016 - 3:28 pm
1. I think you are correct.
2. If it is not listed it is exempted and there is no minimum efficiency required.
This sounds familiar from a previous question in this or another related forum. You might find a more thorough answer.