FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Minimum Energy Performance Calculator – Performance Outputs tab

Greetings,

In the project we are modeling, there are On-site renewable energy production.

In the respective table for filling-in the data related to this production, there is a column heading named Rated Capacity. Should this capacity to be considered as the maximum Peak value or Peak Demand.

Your advice is highly appreciated.

Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/18/2019 - 19:47

The rated capacity of a PV arrary for example, is the total peak value of the rated panel production at optimal conditions. So yes maximum peak value in kW.

Wed, 06/19/2019 - 07:52

"rated" capacity is the capacity measured under a set of laboritory conditions, i.e. at a specific operating point usually specified by some standardized testing proceedure. It's often even more complicated in that the testing proceedure involves reporting the achieved outputs at a range of different operating points and then uses a weighting formula to deturmine the "rated" capacity. So it ties very closely to which standard is put to ground to "rate" the equipment. The idea is that with a standardised rating test, different equipments can be compared to one another for the consumer to know how well they compete.   Your data sheet will usually always show one capacity value that ties in with a set of opperational points/conditions which will also be listed. So for those conditions, the capacity will be valid. When designing, the design capacity is usually the rated capacity, which means the theoretical "worst-case" you would like the equipment to cover. Because it's not practical to always cover every spike, you could consider for example covering the hourly averaged daily "peak". I would try, however, sticking to the datasheet's rated values when entering the date into the table, because they may make more sense for that type of equipment.