GBCI Canada Response
The project team is inquiring if the Minimum Energy Performance Calculator is required for a project intending
to use the zEPI Pilot ACP 143 to demonstrate compliance to ASHRAE 90.1 for EAp Minimum Energy Performance under LEED v4
BD+C.
No. The Minimum Energy Performance Calculator is not required for projects that use zEPI Pilot ACP 143 to
demonstrate compliance for EAp Minimum Energy Performance. However, additional documentation, such as
a detailed modeling report must be provided including all the information and calculations listed in the
Minimum Energy Performance Calculator for the Baseline and Proposed Case.