How do one determine minimum outdoor air intake flow of a VAV system coupled with demand controlled ventilation to comply with ASHRAE 62.12007 standard required for at different operating conditions?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 02/18/2012 - 13:06

Chellapillai, you'll want to ignore the impact of DCV when developing your basic ASHRAE 62.1-2007 compliance calculations. DCV with VAV systems can become challenging to implement properly. It's important to work closely with a controls vendor to include language in sequences of operation that are clear enough to describe intent.