How do one determine minimum outdoor air intake flow of a VAV system coupled with demand controlled ventilation to comply with ASHRAE 62.12007 standard required for at different operating conditions?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
February 18, 2012 - 8:06 am
Chellapillai, you'll want to ignore the impact of DCV when developing your basic ASHRAE 62.1-2007 compliance calculations. DCV with VAV systems can become challenging to implement properly. It's important to work closely with a controls vendor to include language in sequences of operation that are clear enough to describe intent.