CI-2009 EAc3:Measurement and verification

Metering Requirements Case 1

For case 1 (project less than 75% of the total bldg sqft), can temporary metering fulfill the metering requirement? If so, under what circumstances (e.g. minimum monitoring period length, BMS visibility). Reading through the IPMVP for Option D (Calibrated model), the savings are determined by the base case model and the calibrated model. While there is no magic period length for calibrating a model, 3-months of between two seasons can be provide sufficient data variability. If the IPMVP option is satisfied, will the LEED credit be awarded.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/03/2012 - 13:21

Case 1 does not follow the IPMVP. Basically you earn case 1 if you submeter the total energy use of electricity, any fuel and water usage. Temporary meters would not meet the intent of the requirement to provide ongoing accountability.

Tue, 10/16/2012 - 22:56

Thank you for you reply. I have a question about fuels. Heating hot water is monitored by a flow meter, and temperature sensors, however, the gas fired domestic hot water heater does not have metering. In the reference guide it states that "Natural gas, which may be used for both space heating and service heating, can be submetered." Must natural gas be submetered if only used for domestic hot water?

Wed, 10/17/2012 - 13:34

You need to be able to measure gas fuel use in the tenant space even if it is for DHW only. You do not need to measure gas consumption directly if you can make the case that the natural gas usage in the space can be derived from the metering installed.