For EAp3 Building-level Energy Metering on a LEED v4 project, does a propane tank need a meter to meet the requirements of this prerequisite? Would monthly fuel delivery invoices be sufficient to document consumption?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $15.95 »
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5927 thumbs up
October 7, 2021 - 10:33 am
It needs to be metered. Perhaps you could develop a methodology that would determine monthly usage depending on what the fuel is used for. For example if it is for space heating you might be able to use degree day calcaulations to estimate usage. Not sure that would be acceptable however.