Forum discussion

EBOM-2009 WEp1:Minimum indoor plumbing fixture and fitting efficiency

Metering equipment and instruments

We are about to perform the inventory of water flow of the fittings and fixtures in a manufacturing plant. Any recommendations about metering equipment and instruments? Is it possible to install a bypass with a meter on each restroom circuit and then test each fluxometer?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/12/2012 - 14:46

It's up to you to figure out how you'd like to test the flow and flush rates, but the way that I've seen it done in the past is much more low-tech than you're describing. We've simply disconnected the flushometers and used a bucket to catch the water from each flush. For sinks, we'll run the water for 15 seconds and then measure how much is collected and multiple by 2 to get the amount dispensed in 30 seconds. In an ideal exercise, each fixture should be tested 3 times, the results recorded and then averaged to get the average flow/flush rate per fixture. The results for an entire fixture family (i.e. urinals) may then be aggregated to get the average flow/flush rate for the entire facility. At least 20% of the number of fixtures in each fixture family should be tested and, to account for varying water pressure in upper floors of the facility, you should start your testing on the ground floor and work your way up.