Thu, 08/19/2010 - 19:06

No, the credit is still awarded based on the M&V Plan, not the results of the M&V work. Sounds like there is a potential glitch in the form if it won't award the point due to a low percentage of metered energy end-use. In fact the IPMVP does not require that you have permanent meters on any energy end-uses. Some of those energy end uses can be derived through other means such as calculations, spot measurements and short-term trending. You are correct in your assumption about the template regarding energy use information and its relationship to the M&V Plan. If the % compliance is in fact the reason why the form does not register the point then I think the form has a glitch. As I understand it GBCI is still working on the forms and correcting the outstanding issues associated with them.

Thu, 08/19/2010 - 20:20

I believe that the inclusion of reporting for actual energy use in the letter templates is an error. I have advised the USGBC staffers accordingly.

Thu, 08/19/2010 - 20:41

Hi Gord, I am not sure it is an error but I do agree that it would be redundant with the content of the M&V Plan and as such not really necessary.