Forum discussion

CI-2009 IEQc5:Indoor Chemical and Pollutant Source Control

MERV 13 requirement in tall buildings

I am working on a CI project which is in a tall building. The building itself is not LEED certified and the air intakes of the building on 41st floor that provide air to the CI project do not have MERV 13 filters. The intent of this credit is, I believe, prevent hazardous particles that are typically from traffic and other activities surrounding the building that from entering the project space. Would this requirement be still enforced without an exception, even if physical circumstances almost guarantee that the fresh air is unlikely to be polluted at that height (41st floor)? Would it be worth writing a narrative describing that the intent of this credit is fulfilled with the existing filters?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/11/2013 - 16:34

Hi Bilge, I can't speak to air quality at the 41st floor. But I can offer that in our many CIs that occur in parts of uncertified LEED buildings, we have had to install MERV13s on rooftop AHUs that serve our project scope along with other parts of the building to comply. Good luck.

Wed, 12/11/2013 - 16:40

I have also always seen reviewers require MERV 13 no matter the situation circumstances. It never hurts to try a narrative, but I think it's a real long shot.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.