Hi to All,
I would like to clarify the MEPC calculator inputs for LEEDv4 under C&S.
In the Air-Side HVAC tab:
1/ Cooling & heating capacities:
Line 17: Total cooling capacity - do you enter just the capacity of coils in the AHU its self, or include the total capacity, including cooling capacity of terminal units (i.e. FCUs) under that system?
Line 21: Total heating capacity - ditto, the same as above, just for heating.
2/ In the Air-Side HVAC tab: Do you also enter systems that don't serve for ventilation, but just for cooling (i.e. server rooms (not data centres though)), or heating (i.e. radiators) here? I don't see a better place where to include these (unless they are left from the MEPC altogether)?
Thank you,
Lenka
Lenka Matějíčková
Grinity s.r.o. VAT CZ046072282 thumbs up
February 2, 2024 - 4:35 am
Hello again to the forum :) ... any thoughts on the above? Thank you!
Tyler Thumma
7GroupLEEDuser Expert
67 thumbs up
April 5, 2024 - 11:01 am
1. I recommend reporting the AHUs and FCUs in separate columns, that way you can report their capacities separately.
2. Yes, all systems must be reported in the MEPC. Again, I recommend using separate columns for different types of systems.
Lenka Matějíčková
Grinity s.r.o. VAT CZ046072282 thumbs up
April 8, 2024 - 3:19 am
Thank you