We have a project that is struggling to meet the prerequisite requirements of a 20% reduction from the LEEDv4 baseline as the fixtures and fittings are required to be minimum flow rates and flush volumes as required by the English Care Quality Commission (to reduce spread of infection, etc.). Can anyone recommend what steps we could take to achieve the prerequisite if we cannot change the flow rates/flush volumes of fixtures or fittings? Has anyone had experience of the GBCI altering the baseline flow rates/flush volumes for certain projects?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
- The following fixtures can be excluded for all projects:
- Janitor sinks
- Laboratory sinks regulated for medical or industrial purposes
- Soiled utility room flushing rim sinks
- Soiled utility room hand-washing sinks
- Clean utility room hand-washing sinks
- Health care:
- Surgical scrub sinks
- Exam or procedure room sinks for clinical use
- Medication room sinks
- a regular restroom sink would be public (1.9 lpm)
- Patient room sink, and a Patient bathroom sink in hospital or nursing home is private (8.3 lpm)