NC-2009 IEQp1:Minimum indoor air quality performance

Mechanically conditioned space

If you have a MECHANICALLY conditioned space, does it compel you to have MECHANICAL ventilation (not NATURAL)? GH

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/29/2013 - 22:12

No, you are definitely not compelled to have mechanical ventilation just because you have mechanical conditioning. An example is a house with an air conditioner that has operable windows for natural ventilation but no outdoor air intake for mechanical ventilation. I have had a project such as this successfully certified.

Mon, 07/29/2013 - 22:24

For version 2009 there is no requirement to mechanically ventilate when there is mechanical conditioning. ASHRAE 62.1-2010 however, does not allow for this configuration. I guess they caught on that it didnt really make sense for large office spaces. The next version of LEED therefore, will have to mechanically ventilate.