FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Mechanical Ventilation in a Warehouse

Hello,

Maybe this question has already been done, and many times, but can´t find it.

I am modeling a Warehouse which is not conditoned nor heated. It has intake fans to comply with ASHRAE 62.1 and exhaust fans for some specific areas.

The question is: how do I model the Baseline for these fans? Are they process loads for the warehouse or do I have to model them as per Appendix G, G3.1.2.9? and if so, with which baeline system do they match?

Thank you!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/05/2017 - 14:06

They are process fans so the baseline is modeled identically to the proposed design.

Tue, 04/11/2023 - 07:50

Marcus,

I have a question related in warehouse process fan.
Our project team consider process fan consumption (supply, jet, exhaust). The expected that's consumption is so high..
  so I'm Under review about ashrae standard,  G3.1.1 exceptions e : "Thermal zones designed with heating only systems in the proposed design, serving storage rooms, stair­wells, vestibules, electrical/ mechanical rooms, and restrooms not exhausting or transferring air from mechani cally cooled thermal zones in the proposed design shall use System type 9 or 10 in the baseline building design."   Is that point isn't related our case? (Out project space is warehouse which is designed only fans, not heating or cooling)
Best Regards,

Tue, 04/11/2023 - 14:18

If you have no heating only spaces in your project then this exception does not apply.