I'm working in a small project with natural ventilation overall. Considering these 3 facts: 1. LEED states to comply with sections 4-7 of ASHRAE 62.1-2007. 2. Natural ventilation is designed according to section 5.1 of ASHRAE 62.1-2007. 3. Section 6 says: ''This section is not required for natural ventilation systems'' So, my question is: do spaces like toilets, kitchenettes, dressing rooms, etc. need to comply with table 6-4 (minimum exhaust rates) by installing a mechanical exhaust fan? even when they comply with the section 5.1 (4% of operable window)? Thanks in advance!
Ronald, the compliance for naturally ventilated spaces doesn't reference sections 4 through 7, only 5.1. So I think that answers your question? (Note the credit language above.)