I'm working in a small project with natural ventilation overall.
Considering these 3 facts:
1. LEED states to comply with sections 4-7 of ASHRAE 62.1-2007.
2. Natural ventilation is designed according to section 5.1 of ASHRAE 62.1-2007.
3. Section 6 says: ''This section is not required for natural ventilation
systems''
So, my question is: do spaces like toilets, kitchenettes, dressing rooms, etc. need to comply with table 6-4 (minimum exhaust rates) by installing a mechanical exhaust fan? even when they comply with the section 5.1 (4% of operable window)?
Thanks in advance!
Tristan Roberts
RepresentativeVermont House of Representatives
LEEDuser Expert
11477 thumbs up
March 7, 2014 - 11:08 pm
Ronald, the compliance for naturally ventilated spaces doesn't reference sections 4 through 7, only 5.1. So I think that answers your question? (Note the credit language above.)
Ron Dean
Sumac Inc.21 thumbs up
March 14, 2014 - 12:19 pm
Thanks Tristan,
Seccion 5.1 of ASHRAE 62.1-2007 states the requirements for natural ventilation, however I'm still struggling with the scope of such requirements (how about spaces that normally have mechanical exhaust? Are they in the scope of 5.1?)
Does it mean that all spaces including toilets, kitchenettes, etc. need to have the 4% window requirement?
Thanks in advance!