Maximum Temperature

Dear All, I need to ensure that in the 60/60 rule, I do not find anything about the maximum indoor temperature during flush-out, please advice if I can maintain any indoor temperature as long as it is above 60 F.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 05/11/2016 - 12:22

There is no maximum temperature limit for v3 projects. However v4 projects cannot exceed 80 F (27 C).

Thu, 05/12/2016 - 08:05

Thanks David. I need also to know the minimum acceptable measurement interval. Meaning that I will be preparing a log for CFM, Temp, Humidity, and commutative CF over time, and flush-out will take a total of 30 days, so; is it OK to take two readings per day for example?

Thu, 05/12/2016 - 12:21

There is no required minimum measurement interval. However from Landry Watson's post below, GBCI asked for hourly readings during the flushout. Two readings per day should suffice, if taken 12 hours apart and there are no significant outdoor temperature drops and no significant outdoor relative humidity increases.