Hi, based on a water test report, if the number of cycles already exceed 10, does that mean that both points are achievable? The calculations for the project indicate the lowest number of cycles (max. allowed / Test Number) to be 20.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $... »
Ben Stanley
Senior Sustainability ManagerWSP - Built Ecology
LEEDuser Expert
250 thumbs up
January 11, 2018 - 4:24 pm
Yes, if you have already tested the make up water and the cooling tower is operating at 10 cycles or above, you meet the requirements for 2 points.