Hi,
I have an air conditioned warehouse, where wine will be sotored, and it has two doors, with now vestibules.
these doors will be used aproximatly once a week for loading and downloading.
would these doors apply for the Exceptions in Seccion 5.4.3.4., b: "Doors not intended to be used as a building entrance." of the Standard 90.1-2007?,
Thank you
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
March 15, 2012 - 4:52 pm
Doors only used for loading and unloading sound like they qualify for this exception.
Any door used as a building entrance must have a vestibule if it does not qualify for one of the exceptions.