Hello All,
I have two questions about compliance with the mandatory provision:
1) Only the main air conditioning system should be evaluated with the tables in chapter 6? or if I have 2 or 3 small offices with teams split wall, they also must meet?
2) According to section 10.4 must be met given engine efficiency for motor 60Hz, according investigate this table comes from NEMA MG 10-2001 Publication Standars and this in turn is emulated with IEC 60034-30 for 50Hz. Is this correct or do not care if Chile motors low efficiencies are even lower than the IE2?
Thanks for the reply.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
August 17, 2012 - 4:25 pm
1. All system must meet the mandatory minimum efficiency requirements in Tables 6.8.1A to J, no matter the size or effect.
2. I do not know the origin of the motor efficiency values. However, we do care if the motors in your design comply with these efficiency values, since this is mandatory they need to comply.