FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Mandatory for plug fans

Is Table 10.8 mandatory for plug fans of new buildings? The fans are installed in Air Handling Units. If they are mandatory, are they mandatory both for supply fans and for return fans?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/23/2014 - 14:05

Yes the minimum efficiency applies to all HVAC motors 1 HP and up.

Wed, 12/24/2014 - 08:39

Thank you, Marcus. You wrote "motors". Shall we consider the efficiency of Table 10.8 only as the motor efficiency, i.e. the "mechanical power exiting from the motor" / "electric power absorbed by the motor" ratio? I mean, shall we not consider also the fan efficiency, i.e. the "air hydrodynamic power" / "mechanical power exiting from the motor" ratio, in order to verify the mandatory provision? Other issue: when Table 10.8 writes "Motor kilowatts" shall we consider the mechanical power or the electric power?

Wed, 12/24/2014 - 15:52

Table 10.8 lists the motor efficiency and that is all you must comply with. The electrical power I think.

Fri, 01/09/2015 - 11:42

Thank you Marcus, but... new year, old issue... The note of Table 10.8 states: "Nominal efficiencies shall be established in accordance with NEMA Standard MG1". If the motors are not classified according to that standard, but according to IEC 60034-30, how could the mandatory be verified? The motors are classified IE2 and have inverters. Can the increase of efficiency due to the inverters be considered? The project is located in Italy. Could I find some alternative compliance paths for Europe for the mandatory provision for fan motors? Best Regards

Fri, 01/09/2015 - 16:07

I have not attempted to compare the two standards. You have a couple of options - do the comparison yourself so that you can say that you definitively meet this mandatory provision or just assume that the standards are roughly equivalent and indicate that you meet this mandatory provision. One thought is are the motors in question ever exported to the US? If so then they would likely have to meet the NEMA Standard. Perhaps the motor manufacturer could be of assistance. I can tell you that the motor efficiency mandatory provision is rarely even evaluated during the LEED review as there is no reporting associated with it. The European LEED ACPs outline a process for trying to determine equivalency with 90.1. I think the intention was to determine equivalency at the whole building levels and not necessarily at the component level. http://www.usgbc.org/resources/leed-2009-bdc-supplemental-reference-guide-alternative-compliance-paths-europe