CI-2009 EAc1.1:Optimize energy performance - lighting power

LPD Calculation - Task lightings?

Our project is pursuing IEQ C6.1 (Controllability of Systems - Lightings) and therefore task lightings will be provided. Do we need to consider task lightings on LPD calculation?

5

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/17/2011 - 15:03

Yes. You will have to include them unless you have a the task lights controlled by motion sensors. It's an exception in ASHREA 90.1 2007

Tue, 07/03/2012 - 17:23

Hi Susan, We have received review comments asking us to include the task lighting in the the LPD even when we are showing the ASHRAE motion sensor exemption. We are currently trying to rebut the comment. Besides reiterating the ASHRAE exemption, what would you recommend to show you have controllability and can still exclude task lights from the LPD? Thanks