Local Jurisdiction Approval?

Hi, What is "the local jurisdiction approval"? You know what this is? How do I get this approval? With the designer? I've worked in other certificate were accepted sizing calculations showing the natural ventilation system only. Thank you!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/18/2014 - 15:33

Ivan, 1) Show that the project complies with local jurisdictional, minimum ventilation requirements, if the local requirements exist. 2) Show that the project complies with the LEED/ASHRAE minimum ventilation requirements. Since the project complies with both LEED and local requirements "whichever is more stringent" is proven. There is no reason to compare the two sets of requirements to each other.

Thu, 09/18/2014 - 16:28

Thanks Hernando. The situation I have is that I have a project of a warehouse where there is natural ventilation in coverage. This ventilation is "Enginnered Natural Ventilation System". I showed all sizing calculations, and was asked about this approval of jurisdiction. This ventilation is an exception from section 5.1 of ASHRAE 62.1 but do not know how to prove this, since the document submitted is the natural ventilation calculation description, considering all of the local climate parameters. I need to ask something the ventilation designer, or just explain better what was considered? Best Regards.

Thu, 09/18/2014 - 17:25

Ivan, You can compare the design air changes per hour (ACH) to the Vot (zone outdoor air flow) calculated using the ASHRAE 62.1 calculations: Sections 6.2.2 (Vbz = [Rp x Pz] + [Ra x Az]; and then Voz=Vbz/Ez) and either 6.2.3 (Single-Zone) or 6.2.4 (100% OA). Vot will likely be equal to Voz. Your Ez is probably 0.8 (see ASHRAE 62.1 Table 6-2). It might be 1.0 but claiming a lower Ez helps avoid further questions from the reviewers.

Thu, 09/18/2014 - 17:34

Ok! Now i know how to prove this. This helped a lot. Thanks Hernando!