NC-2009 IEQp1:Minimum IAQ Performance

local code IEQ requirements

In New York the local code does not follow IBC or ASHRAE 62.1. It requires 20cfm/person and 0cfm/sf. How do I go about proving to USGBC that the ventilation levels are adeqaute, when all the template references is 62.1 and the 62MZcalc?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/09/2011 - 14:17

You'll want to use all of the ASHRAE 62.1 calculation methods and then compare the ventilation rates to NYC codes on a zone and system level. The NYC code rates tend to end up being higher than ASHRAE 62.1 rates. For NYC code, application of 403.3.2 (multiple-spaces approach) will result in high system-level ventilation rates.