FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Lighting for Dormitories

LEED Interpretations state that hard-wired lighting in residential units must be modeled identically in the baseline and proposed cases. Does this apply to college dormitories as well? Specifically when all of the lighting will be hard wired and the students are not expected to have any lighting plugged into receptacles.

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/07/2013 - 18:39

Technically this does not apply to a dorm. There is a dorm lighting power density for the living quarters in Table 9.6.1. In my experience it is unrealistic to expect that the students will not bring plug in task lighting so you should model an allowance for it as well.

Thu, 08/08/2013 - 07:20

How does Table 9.5.1 "Multifamily" or Table 9.6.1 Building Specific Space Types "Hotel" or "Dormitory--Living Quarters" fit into the first statement? Secondly, as one or more building area method building types can be used, but building area method and space by space methods may not be mixed, could one use the building area method for the residential part of a building (one building type) and a space by space method for the non-residential part of the building (the other building type)?

Thu, 08/08/2013 - 13:57

A dorm is not considered multifamily. They are both different types of residential projects. I think that would be mixing BAM and SBSM to use one for one part of the building and the other for the remainder.

Thu, 08/08/2013 - 14:33

Let's say I WANT to do space by space for EVERYTHING. But I have one thermal zone for each residential unit. Where does that leave me?

Thu, 08/08/2013 - 14:45

You can use 1.1 W/sf for the residential units but you follow these guidelines if you want to claim any savings within the residential unit - http://new.usgbc.org/resources/energy-star-multifamily-high-rise-simulation-guidelines-v10-eap1-alternative-compliance-pa

Thu, 08/08/2013 - 15:57

I've read those before, but was un-aware of this alternative path. Thanks. Did you mean 2W/sf? Where does 1.1 W/sf come from? Table 5-10 of U.S. Lighting Market Characterization: Volume 1: National Lighting Inventory and Energy Consumption Estimate by Navigant Consulting gives the value of 2.0W/SF as a typical installed wattage in multif amily buildings. The LEED ruling to a Credit Interpretation Request allows using 2.0W/SF as a Baseline for lighting performance credit in residential units